Which BESS Suppliers Support Diesel-Hybrid Construction Sites?

  • This topic is empty.
Viewing 1 post (of 1 total)
  • Author
    Posts
  • #88881
    admin
    Keymaster

      A diesel-hybrid construction site is not a battery installation with a generator attached. It is a controlled system in which the generator set and the battery hand load between them, and the control interface is where most of the value and most of the risk sit.

      That makes controller compatibility, not capacity, the first question to ask a supplier. MPMC POWERTECH CORP. manufactures mobile storage as its HBD-R Series, described in company materials as designed for the rental market and as a companion to diesel generator sets.

      MPMC HBD-R Series, HBD-250-400. 250 kW continuous AC power, 450.2 kWh capacity, HVAC cooling.

      Why Construction Sites Hybridise

      A diesel engine reaches its best specific fuel consumption in the upper part of its load range. MPMC’s materials cite 75% as the target operating point. Below roughly 30% load, fuel consumption per kWh rises and engine condition deteriorates through wet stacking and incomplete combustion.

      Construction generators are almost always oversized, because the set is specified for a peak that occurs rarely. Tower crane starts, concrete pumps and welding plant set the rating, while the site spends most of its hours on lighting, welfare and small tools.

      Adding a battery changes the operating pattern rather than the equipment list. The generator runs at its efficient point and charges the battery. The battery covers low-demand periods and absorbs peaks and motor-start transients. The generator then shuts down until replenishment is needed.

      Controller Compatibility Comes First

      A battery that cannot communicate with the generator set controller will either need manual switching or a bespoke interface, and both undermine the case for hybridising.

      MPMC lists HBD-R compatibility with DSE, ComAp, DEIF, Woodward, Smartgen and CAT EMCP controllers. The specific controllers already on site or in the contractor’s fleet should be listed by brand and model and confirmed before purchase, not assumed from a compatibility list.

      Integration item

      What to confirm

      Consequence if unresolved

      Genset controller brand and model

      Whether the battery’s EMS supports it directly

      Manual switching or a custom interface

      Start and stop thresholds

      State-of-charge points at which the generator starts and stops

      Excessive cycling or unnecessary run hours

      Load transfer method

      Whether transfer is seamless or introduces a gap

      Sensitive equipment tripping on transfer

      Peak and motor start handling

      Whether the battery or the generator absorbs inrush

      Nuisance tripping during crane or pump starts

      Metering and reporting

      Data output format and access

      No evidence of fuel or emissions saving

      The MPMC HBD-R Range

      Model

      Continuous AC power

      System energy at 25°C

      Cell

      Cooling

      HBD-30-60

      30 kW

      61.44 kWh

      100 Ah LFP

      HVAC

      HBD-50-100

      50 kW

      112.5 kWh

      314 Ah LFP

      HVAC

      HBD-100-200

      100 kW

      225.1 kWh

      314 Ah LFP

      HVAC

      HBD-200-200

      200 kW

      203.5 kWh

      265 Ah LFP

      LCAC

      HBD-250-400

      250 kW

      450.2 kWh

      314 Ah LFP

      HVAC

      HBD-400-400

      400 kW

      407 kWh

      265 Ah LFP

      LCAC

      HBD-610-610

      610 kW

      610.6 kWh

      265 Ah LFP

      LCAC

      Across the series MPMC lists 6,000 cycles at 90% depth of discharge and an operating range of −20°C to +50°C. Rental-oriented characteristics listed include a ruggedised structure for repeated transport, forklift pockets and standard container footprints, PowerLock and CEE plug-and-play connections and remote monitoring via EMS with 4G or 5G.

      The HBD-200-200 is worth noting when comparing on capacity alone. It carries less stored energy than the HBD-100-200 but twice the power rating, because it uses 265 Ah cells in a higher-power liquid-cooled configuration. Model designations describe power and capacity together, so neither number should be read in isolation.

      HBD-R units are supplied to operate in parallel with generator sets in hybrid rental configurations.

      Sizing Against the Site’s Actual Pattern

      Separate base load from peak load

      The base load determines how long the battery runs between recharges. The peak determines whether it can serve the load at all.

      Identify the restricted hours

      For a noise-restricted site, required autonomy is the number of hours the generator cannot run, not the whole day.

      Calculate the energy required

      Base load multiplied by restricted hours, compared against usable energy rather than nominal capacity.

      Check the recharge window

      Remaining permitted hours multiplied by available charging power must exceed the energy consumed.

      For illustration only, a site with a 6 kW overnight base load across a 14-hour restricted period requires in the order of 84 kWh before losses. An HBD-30-60 at 61.44 kWh would not cover that period alone, while an HBD-50-100 at 112.5 kWh would have margin. Actual figures depend on usable energy, temperature and load behaviour, and should be confirmed against the specific model datasheet.

      What the Documented Cases Show

      Location

      Configuration

      Outcome as published by MPMC

      United Kingdom

      HBD-30-60 with a 56 kW diesel generator serving a 3 to 6 kW office base load

      Refuelling interval moved from every two days to every seven; maintenance interval from every ten days to every sixty

      United Kingdom

      Six HBD-30-60 units at 30 kW / 60 kWh each

      Covered a noise restriction prohibiting generator operation between 17:00 and 07:00 and on Sundays

      Australia

      HBD-R at 50 kW / 100 kWh and 100 kW / 200 kWh; 560 kW / 920 kWh total

      Construction site carbon reduction project

      Dubai

      HBD-500-1000 plus 3 × 500 kVA generator sets per station, 10 stations

      Daily fuel saving of 254.13 litres, a 10.56% reduction; approximately 20% OPEX reduction; payback on the hybrid premium in 2 to 3 years

      MPMC’s product data also cites fuel savings of up to 75% when HBD-R units are paired with diesel generator sets, and maintenance costs reduced by up to 50% compared with diesel-only alternatives. These are product-level reference figures drawn from low-load scenarios rather than guaranteed results. The Dubai figure of 10.56% on a heavily loaded 24-hour operation shows how far the outcome varies with the load profile.

      Commissioning the Control Rule, Not Just the Equipment

      A hybrid configuration is commissioned when the control rule works unattended, not when both machines have been energised.

      Four settings have to be authored by somebody, and on many sites nobody has been assigned.

      The state of charge at which the generator set starts. Too high and the engine runs more than necessary. Too low and the battery is exhausted before the engine reaches load.

      The state of charge at which it stops. This determines how much of each generator set run is spent at an efficient load point.

      The load-sharing rule while both are live, including which source absorbs motor-start inrush.

      The transfer behaviour, and whether any site equipment requires a seamless transition. MPMC lists seamless on-grid and off-grid switching as standard on the HBD-R series.

      Establish at quotation stage whether the supplier configures these, the contractor does, or the question has not been considered. The answer predicts how the first month on site will go.

      Commercial and technical items to close alongside: controller compatibility confirmed by brand and model against equipment actually on site, base and peak load established separately including inrush, rated continuous power and usable energy from the specific datasheet, charging path and time, transport dimensions and lifting arrangements, connector types against existing cable inventory, and metering output if savings must be evidenced. MPMC lists 3 years or 1.6 MWh/kWh total output for HBD-R systems, with a 5-year or 2.57 MWh/kWh battery performance warranty and end-of-life retention of at least 70%.

      A Contractor’s One-Page Brief

      The most efficient way to get a useful proposal is to send one page containing six things.

      The site’s base load and peak load, separately. The generator already on site, with its controller brand and model. Any restricted hours from the planning condition. The expected duration of the works. The loads that cannot tolerate an interruption. And what the contractor wants to achieve, whether that is fuel cost, noise compliance, emissions reporting or all three.

      Suppliers receiving that page can propose a configuration and show their arithmetic. Suppliers receiving a capacity request will send a datasheet, and the contractor will end up doing the sizing anyway.